Radial well aquifer benchmark (Water Module): Difference between revisions
| (19 intermediate revisions by 2 users not shown) | |||
This | This [[Water_Module_benchmarks|benchmark]] demonstrates a situation where a well is extracting ground water. A characteristic ground water level curve will form over time. | ||
[[File:drainage_freatic_benchmark.gif]] | [[File:drainage_freatic_benchmark.gif]] | ||
{{clear}} | |||
===Formulas=== | ===Formulas=== | ||
Stationary lowering of the ground water table in a closed water transmissive layer can be described by the following formula | Stationary lowering of the ground water table in a closed water transmissive layer can be described by the following formula{{ref|verruijt70}} | ||
<math>\phi(r) - \phi_0 = \frac {Q_0}{2\pi\cdot kD} \ln{\left ( \frac{r}{R} \right )}</math> | <math>\phi(r) - \phi_0 = \frac {Q_0}{2\pi\cdot kD} \ln{\left ( \frac{r}{R} \right )}</math> | ||
where: | where: | ||
: <math> | : <math>phi_0</math>: stable water level at the considered stable water table edge | ||
: <math>phi(r)</math>: water level between the considered stable water table edge and the well | : <math>phi(r)</math>: water level between the considered stable water table edge and the well | ||
: <math>kD</math>: transmissivity of the aquifer in m² / day | : <math>kD</math>: transmissivity of the aquifer in m² / day | ||
: <math>r</math>: distance to the well | : <math>r</math>: distance to the well | ||
| Line 20: | Line 19: | ||
===Setup=== | ===Setup=== | ||
We use the following setup in our tests. The grid size used is 51 by 51, with a configurable cell size of <math>dx</math> in meters. There is one underground outlet, which pumps water away continuously with a default amount per second. | We use the following setup in our tests. The grid size used is 51 by 51, with a configurable cell size of <math>dx</math> in meters. There is one underground outlet, which pumps water away continuously with a default amount per second. | ||
The terrain height is set to 0 meters (datum). | |||
The outlet is placed on the cells x = 25 and y = 25 as an [[Inlet (Water Overlay)|inlet]] with a negative inlet. | The outlet is placed on the cells x = 25 and y = 25 as an [[Inlet (Water Overlay)|inlet]] with a negative inlet. | ||
[[Inlet q (Water Overlay)| | :[[Inlet q (Water Overlay)|INLET Q]] is set to <math>\frac{-Q_0}{3600*24}</math> | ||
:[[Inlet underground (Water Overlay)|UNDERGROUND]] is set to true (1.0) to place the outlet below the surface. | |||
To stabilized the water levels on the edges of the test case , an additional underground inlet is used. It is located on all cells equal to or further away than the chosen R. | |||
This inlet is configured as followed: | |||
:[[Inlet q (Water Overlay)|Inlet Q]] set to 0, such that is unlimited. | |||
:[[Inlet_upper_threshold_(Water_Overlay)|UPPER_THRESHOLD]] set to -2 m. | |||
:[[Inlet_lower_threshold_(Water_Overlay)|LOWER_THRESHOLD]] set to -2 m. | |||
The [[Ground bottom distance m (Water Overlay)|ground bottom distance]] is configured as 10 meters, which places the bottom at -10 meters (datum). | |||
The [[Terrain water storage percentage (Water Overlay)|water storage fraction]] is set to 0.25. | |||
An [[Aquifer (Water Overlay)|aquifer]] can be added to configure the [[Aquifer kd (Water Overlay)|kD]] value used in the test. | |||
The simulation is run for 64 days with 0 rainfall, which is configured in the weather's [[Weather rain m (Water Overlay)|rain attribute]] as: <math>[64 \cdot 24 \cdot 3600, 0]</math> | |||
===Test results=== | |||
Important in all these tests is the chosen R, which is the distance to the well that is considered a stable water level. Additionally, the measurements are done relative to the [[Bottom distance prequel (Water Overlay)|bottom boundary]], which is situated 10 meters below the surface. | |||
====Test case 1==== | |||
:cell size: 5 m; | |||
:<math>kD</math>: 88 m²/day; | |||
:<math>R</math>: 110; | |||
:<math>Q_0</math>: 50; | |||
:Simulation days <math>n</math>: 64 days; | |||
[[File:5m_50m3_88kd.png]] | |||
====Test case 2==== | |||
:<math>kD</math>: 44 m²/day; | |||
[[File:5m_50m3_44kd.png]] | |||
====Test case 3==== | |||
:<math>kD</math>: 22 m²/day; | |||
[[File:5m_50m3_22kd.png]] | |||
====Test case 4==== | |||
:<math>kD</math>: 11 m²/day; | |||
[[File:5m_50m3_11kd.png]] | |||
====Test case 5==== | |||
:<math>Q_0</math>: 25; | |||
[[File:5m_25m3_22kd.png]] | |||
====Test case 6==== | |||
:<math>Q_0</math>: 100; | |||
[[File:5m_100m3_22kd.png]] | |||
====Test case 7==== | |||
:cell size: 2 m; | |||
:<math>Q_0</math>: 1; | |||
[[File:2m_1m3_22kd.png]] | |||
====Test case 8==== | |||
:<math>Q_0</math>: 16; | |||
[[File:2m_16m3_22kd.png]] | |||
====Test case 9==== | |||
:<math>Q_0</math>: 4; | |||
[[File:2m_4m3_22kd.png]] | |||
====Test case 10==== | |||
[[File:2m_4m3_44kd.png]] | |||
====Test case 11==== | |||
[[File:2m_4m3_88kd.png]] | |||
{{article end | |||
|references= | |||
<references> | <references> | ||
{{ref|verruijt70 | |||
|name=Theory of Groundwater Flow. Macmillan, London | |||
|author=Verruijt, A. (1970) | |||
|page= | |||
|source= | |||
|link= | |||
|lastvisit= | |||
{{Water Module buttons}} | {{Water Module buttons}} | ||
Latest revision as of 11:26, 17 October 2025
This benchmark demonstrates a situation where a well is extracting ground water. A characteristic ground water level curve will form over time.
Stationary lowering of the ground water table in a closed water transmissive layer can be described by the following formula[1]
- : stable water level at the considered stable water table edge
- : water level between the considered stable water table edge and the well
- : transmissivity of the aquifer in m² / day
- : distance to the well
- : distance of the considered stable water table edge to the well
- : amount of water pumped out in m³ / day
Setup
We use the following setup in our tests. The grid size used is 51 by 51, with a configurable cell size of in meters. There is one underground outlet, which pumps water away continuously with a default amount per second.
The outlet is placed on the cells x = 25 and y = 25 as an inlet with a negative inlet.
- INLET Q is set to
- UNDERGROUND is set to true (1.0) to place the outlet below the surface.
To stabilized the water levels on the edges of the test case , an additional underground inlet is used. It is located on all cells equal to or further away than the chosen R. This inlet is configured as followed:
- Inlet Q set to 0, such that is unlimited.
- UPPER_THRESHOLD set to -2 m.
- LOWER_THRESHOLD set to -2 m.
The ground bottom distance is configured as 10 meters, which places the bottom at -10 meters (datum).
The water storage fraction is set to 0.25.
An aquifer can be added to configure the kD value used in the test.
The simulation is run for 64 days with 0 rainfall, which is configured in the weather's rain attribute as:
Test results
Important in all these tests is the chosen R, which is the distance to the well that is considered a stable water level. Additionally, the measurements are done relative to the bottom boundary, which is situated 10 meters below the surface.
Test case 1
- cell size: 5 m;
- : 88 m²/day;
- : 110;
- : 50;
- Simulation days : 64 days;
Test case 2
- cell size: 5 m;
- : 44 m²/day;
- : 110;
- : 50;
Test case 3
- cell size: 5 m;
- : 22 m²/day;
- : 110;
- : 50;
Test case 4
- cell size: 5 m;
- : 11 m²/day;
- : 110;
- : 50;
Test case 5
- cell size: 5 m;
- : 22 m²/day;
- : 110;
- : 25;
Test case 6
- cell size: 5 m;
- : 22 m²/day;
- : 110;
- : 100;
Test case 7
- cell size: 2 m;
- : 22 m²/day;
- : 110;
- : 1;
Test case 8
- cell size: 2 m;
- : 22 m²/day;
- : 110;
- : 16;
Test case 9
- cell size: 2 m;
- : 22 m²/day;
- : 110;
- : 4;
Test case 10
- cell size: 2 m;
- : 44 m²/day;
- : 110;
- : 4;
Test case 11
- cell size: 2 m;
- : 88 m²/day;
- : 110;
- : 4;
- ↑ Theory of Groundwater Flow. Macmillan, London ∙ Verruijt, A. (1970)