Radial well aquifer benchmark (Water Module): Difference between revisions
(8 intermediate revisions by 2 users not shown)
This testcase demonstrates a situation where a well is pumping up ground water. A characteristic ground water level curve will form over time.
This [[Water_Module_benchmarks|benchmark]] demonstrates a situation where a well is extracting ground water. A characteristic ground water level curve will form over time.
[[File:drainage_freatic_benchmark.gif]]
<br style="clear:both;">
{{clear}}
===Formulas===
===Formulas===
Stationary lowering of the ground water table in a closed water transmissive layer can be described by the following formula <ref name="verruijt70"/>
Stationary lowering of the ground water table in a closed water transmissive layer can be described by the following formula{{ref|verruijt70}}
<math>\phi(r) - \phi_0 = \frac {Q_0}{2\pi\cdot kD} \ln{\left ( \frac{r}{R} \right )}</math>
: <math>phi(0)</math>: stable water level at the considered stable water table edge
: <math>phi_0</math>: stable water level at the considered stable water table edge
: <math>phi(r)</math>: water level between the considered stable water table edge and the well
: <math>phi(rw)</math>: water level in the well
: <math>kD</math>: transmissivity of the aquifer in m² / day
: <math>r</math>: distance to the well
Line 44: Line 43:
===Test results===
===Test results===
Important in all these tests in the chosen R, which is the distance to the well that is considered a stable water level. Additionally, the measurements are done relative to the impenetrable soil, which is situated 10 meters below the surface.
Important in all these tests is the chosen R, which is the distance to the well that is considered a stable water level. Additionally, the measurements are done relative to the [[Bottom distance prequel (Water Overlay)|bottom boundary]], which is situated 10 meters below the surface.
====Test case 1====
====Test case 1====
Line 134: Line 133:
[[File:2m_4m3_88kd.png]]
===References===
|references=
<references>
<references>
<ref name="verruijt70>Verruijt, A. (1970). Theory of Groundwater Flow. Macmillan, London.</ref>
{{ref|verruijt70
  |name=Theory of Groundwater Flow. Macmillan, London
  |author=Verruijt, A. (1970)
  |page=
  |source=
  |link=
  |lastvisit=
</references>
</references>
{{Water Module buttons}}
Latest revision as of 11:26, 17 October 2025
This benchmark demonstrates a situation where a well is extracting ground water. A characteristic ground water level curve will form over time.
Stationary lowering of the ground water table in a closed water transmissive layer can be described by the following formula[1]
ϕ(r)ϕ0=Q02πkDln(rR)
phi0: stable water level at the considered stable water table edge
phi(r): water level between the considered stable water table edge and the well
kD: transmissivity of the aquifer in m² / day
r: distance to the well
R: distance of the considered stable water table edge to the well
Q0: amount of water pumped out in m³ / day
Setup
We use the following setup in our tests. The grid size used is 51 by 51, with a configurable cell size of dx in meters. There is one underground outlet, which pumps water away continuously with a default amount per second.
The terrain height is set to 0 meters (datum).
The outlet is placed on the cells x = 25 and y = 25 as an inlet with a negative inlet.
INLET Q is set to Q03600*24
UNDERGROUND is set to true (1.0) to place the outlet below the surface.
To stabilized the water levels on the edges of the test case , an additional underground inlet is used. It is located on all cells equal to or further away than the chosen R. This inlet is configured as followed:
Inlet Q set to 0, such that is unlimited.
UPPER_THRESHOLD set to -2 m.
LOWER_THRESHOLD set to -2 m.
The ground bottom distance is configured as 10 meters, which places the bottom at -10 meters (datum).
The water storage fraction is set to 0.25.
An aquifer can be added to configure the kD value used in the test.
The simulation is run for 64 days with 0 rainfall, which is configured in the weather's rain attribute as: [64243600,0]
Test results
Important in all these tests is the chosen R, which is the distance to the well that is considered a stable water level. Additionally, the measurements are done relative to the bottom boundary, which is situated 10 meters below the surface.
Test case 1
cell size: 5 m;
kD: 88 m²/day;
R: 110;
Q0: 50;
Simulation days n: 64 days;
Test case 2
cell size: 5 m;
kD: 44 m²/day;
R: 110;
Q0: 50;
Test case 3
cell size: 5 m;
kD: 22 m²/day;
R: 110;
Q0: 50;
Test case 4
cell size: 5 m;
kD: 11 m²/day;
R: 110;
Q0: 50;
Test case 5
cell size: 5 m;
kD: 22 m²/day;
R: 110;
Q0: 25;
Test case 6
cell size: 5 m;
kD: 22 m²/day;
R: 110;
Q0: 100;
Test case 7
cell size: 2 m;
kD: 22 m²/day;
R: 110;
Q0: 1;
Test case 8
cell size: 2 m;
kD: 22 m²/day;
R: 110;
Q0: 16;
Test case 9
cell size: 2 m;
kD: 22 m²/day;
R: 110;
Q0: 4;
Test case 10
cell size: 2 m;
kD: 44 m²/day;
R: 110;
Q0: 4;
Test case 11
cell size: 2 m;
kD: 88 m²/day;
R: 110;
Q0: 4;
  1. Theory of Groundwater Flow. Macmillan, London ∙ Verruijt, A. (1970)