Line 1,551: | Line 1,551: | ||
* ΔB = The calculated width increase of the breach. | * ΔB = The calculated width increase of the breach. | ||
* H = | * H = The difference between the height of the water columns on either side of the breach. | ||
* MF = Material factor, set to 1.3 (average for sand and clay levees) | * MF = Material factor, set to 1.3 (average for sand and clay levees) |
Revision as of 10:18, 8 March 2019
What is the Water overlay
Water flow is affected by properties of the surface across which it flows, including the terrain height and the properties of the underlying terrain.
Variants
- Rainfall Overlay, provides insight into the water stress caused by (excessive) rainfall.
- Flooding Overlay, provides insight into water stress caused by breaches in levees or other sources causing excessive water inflow.
- Groundwater Overlay, provides insight into long-term processes of water flow both on the surface and underground.
Use cases
- Main article: Use cases Water Overlay
How to use the Water overlay
Prerequisites
- Your project has been loaded in with a high-resolution DEM. This can be configured during the new project wizard.
- Your project is large enough to account for edge effects.
- When creating a new project in the new project wizard, consider using the AHN3 dataset rather than the default AHN2. Where coverage is available, the AHN3 dataset will be more accurate. Where coverage is not available, the default AHN2 should be used.
- Additionally, when creating a new project, consider whether you want to use the IMWA dataset for hydrological constructions. Although this dataset is not complete, some information about constructions which serve as culverts other relevant objects can be loaded in from this datasource. If more complete or accurate data is available to be loaded in into the project after it is created, it may be desirable to disregard this source so that hydrological constructions are not doubly included.
- Water flow can often be dictated by small features in an area, such as small openings between buildings, and thin levees. To have these small features included properly in the calculations, the grid cell size will need to be set to an appropriate size. The default setting offered by the Tygron Platform will often need to be adjusted to allow for smaller features to be recognized without having their presence averaged out with their surroundings.
- The water overlay performs a complete simulation, which is a series of complex calculations across multiple layers. Depending on the configuration of the overlay, the calculation time can range from seconds to hours. If the overlay is to be used in a setting where response times need to be short, it may be preferable to configure the overlay for greater speed rather than excessive precision.
Configuration
Configuration wizard
Step 1: Weather
Step 2: Water system
- Breach (flooding overlays only): A breach, a location where an (uncontrolled) inflow of water takes places, can be imported or connected to the hydrological model.
- Water areas: Water level areas, defined regions in which a specific water level is maintained, can be imported or connected to the hydrological model. It is also possible to have the wizard generate a single water level area for the entire project area.
- Ground water: Ground water, the height of the underground saturated by water, relative to datum. A GeoTIFF can be imported.
- Sewers: Sewer areas, the broad definitions for where what kind of sewers exist, can be imported or connected to the hydrological model. It is also possible to have the wizard generate sewer areas based on the neighborhoods in the project area.
- Inundation areas: Inundation areas, definitions of water on the surface, in the forum of inundated land, can be imported or connected to the hydrological model. It is also possible to have the wizard generate a single inundation area covering the entire project area.
- Aquifer areas: Aquifer areas, definitions for transmissivity or hydraulic conductivity of the underground layer.
- Weirs: Weirs, minor barriers in the water flow, can be imported or connected to the hydrological model.
- Culverts: Culverts, tunnels which form direct connections between two locations, can be imported or connected to the hydrological model.
- Pumps: Pumps, structures which move water from a lower to a higher location, can be imported or connected to the hydrological model.
- Inlets: Inlets, structures which add or remove water, can be imported or connected to the hydrological model.
- Sewer overflows: Sewer overflows, points where water from sewers can flow back onto the surface, can be imported or connected to the hydrological model.
- Surface terrain: For the surface terrains, attributes can be adjusted directly.
- Underground terrain: For the underground terrains, attributes can be adjusted directly as well.
- Constructions: For constructions, the wizard links to the function values editing screen, and will open it the "WATER" filter for the values to display.
Step 4: Interaction
Step 5: Output overlays
Multiple result types are available. In the wizard multiple result types can be selected. One result type (indicated with the "First" checkbox) will be the main overlay's result type. The other selections will become result child overlays. Relevant attributes can be modified as well, if they are related to selected result types.
Step 6: Input overlays
To gain more insight into the data used by the model, you may opt to add one or more input overlays as well. These add Average Overlays configured for the geographical display of attribute values relevant for the calculation of the water model.
Manual configuration
Besides using the configuration wizard, it is also possible to configure a number of settings manually. A few settings can only be changed manually. Besides the data of geographical features, which have their own means of loading in depending on their type, all manual configuration options are listed here.
Grid cell size configuration
- Main article: Grid overlay
- Main section: Calculation preference formula
- Main section: Weather
Template:Editor ribbon The weather configuration, which dictates the duration of the simulation, the amount of rain and the evaporation rate, is modeled as a separate weather object which is connected to the water overlay. The weather object can be replaced with another, changing the main simulation and weather properties. The weather itself can be changed as well.
Ground water configuration
- Main section: Ground water
Subsidence configuration
- Main section: Subsidence
- Main section: System visualization
Active in simulation setting
Result type configuration
- Main section: Result type
Note that via the configuration wizard multiple result types can be added in parallel in the form of result child overlays.
Legend configuration
Keys configuration
- Main section: Keys
Attributes configuration
- Main section: Attributes
Template:Editor ribbon The water model's calculations make use of a number of centralized parameters, which are configured as attributes of the overlay. Depending on the exact variants of the water overlay, some of the parameters will have different defaults to better suit the exact type of calculation. The parameters can be tweaked further to better fit specific use-cases, but in general the defaults are appropriate for most calculations.
Results
When the calculation completes, the results are stored as numerical values in a grid spanning the entire 3D world. The exact values and their meanings depend on the selected result type. Each timeframe and each result child overlays has it's own grid of data. There are multiple ways to interact with this data. In addition, there are a few additional outputs provided by the water overlay specifically to gain further insight, verification, and visualization of the results.
Geographical overview
Visualization
Depending on whether the option is selected, the hydrological system can be visualized when when the overlay is activated. Each water level area will be visualized by a blue floating sphere and a striped border along the surface of the terrain. Sewer areas are visualized by an orange floating sphere. If the sewer has a sewer overflow, the overflow is connected to the sewer's sphere via an orange line. Culverts, weirs, and pumps are visualized by green, orange, and red spheres respectively for their endpoints, connected by blue lines.
Hover panel
- The ground height, which is the terrain height relative to datum.
- The output value of the overlay, which is dependent on the selected result type.
- The hydrological properties of the terrain (if applicable), such as manning value and infiltration speed.
- The hydrological properties of features (if applicable), such as water level, inundation level, and altered terrain height.
- The hydrological properties of constructions (if applicable), such as building storage, and sewer storage of sewered buildings.
Detailed results
Timeframes
Note that the simulation time is divided into a TIMEFRAMES amount of periods, and at the end of each period a timeframe is recorded. This means the first timeframe is not a snapshot of the initial state of the simulation, but a snapshow of the state of the simulation after the first period of time has passed already.
TQL
- Main article: TQL
Measuring tool
- Main article: Measuring tool
While viewing the overlay, a general impression of the values can be seen at a glance. However, depending on the configuration of the overlay's legend the exact values may be difficult to view exactly. Using the measuring tool it's possible to retrieve the values of the overlay on exact locations. Additionally, cross-sections can be defined and easily have their values inspected.
Exporting Geotiff
Additional forms of output
A number of output forms don't fit in the analysis structure described above, but can provide additional information or insight into the calculation. These can provide different ways of looking at both the input and output of the simulation. They are offered as a means to further visualize but also verify the performed calculations.
Weather visualization
Saving overlay result
Water balance
Input | Output |
Debug info
After the calculation completes, some additional information is tallied and output for debugging purposes. This is intended for verification that the model has computed as expected, and may provide some basic information at a glance. It is not meant as a primary tool for in-depth analysis of the results.
The following information is displayed:
Debug info |
Input overlay
- Main article: Average Overlay
The water overlay's calculations rely on multiple geographical parameters, such as manning values and evaporation factors. To help with both understanding the outcome of the calculation as well as verifying the results, the configuration wizard offers the option to add input overlays to the project, which are Average Overlays configured to display the input parameters geographically.
Overlays such as these can also be created manually, by creating an Average Overlay and configuring it such that it functions on the desired attribute, and with an as small an averaging distance as possible. Optionally, a specific layer (such as constructions or terrains) can be configured which the overlay should inspect.
Model connections
The hydrological model can be linked to other models, which adds and defines more data for the simulation. Some models are automatically connected, and are required for the calculations to take place. Others are optional, and can apply additional detail to the calculations. When the optional models are absent, default behavior is defined.
Terrain height
- Main article: Terrain height
Weather
Rain and simulation time
Linear configuration
Property | Unit | Description |
Rain for | minutes | How long rain should last at the start of the simulation. |
Total rainfall | mm | How much rain should fall in the specified period. |
Dry after rain (days, hours, minutes) | days, hours, minutes | How long the simulation continues after the rain has fallen. |
Custom configuration
Rain and simulation CSV specification | |||||||||
Data per line | Additional rainfall until specified moment | ||||||||
Criteria | Time should always be greater than or equal to previous time Rain should never be negative | ||||||||
First entry | Second entry | ||||||||
Time (s) | Rain (m) | ||||||||
Line 1 | Time when first period ends | Total rain during first period | |||||||
Line 2 | Time when second period ends | Total rain during second period |
Evaporation rate
Surface evaporation | mm/day | The speed at which water evaporates during the simulation |
Evaporation CSV specification | |||||||||
Data per line | Rate of evaporation until specified moment | ||||||||
Criteria | Time should always be greater than or equal to previous time Evaporation should never be negative | ||||||||
Time (s) | Evaporation (m) | ||||||||
Line 1 | Time when first period ends | Amount of evaporation during first period | |||||||
Line 2 | Time when second period ends | Amount of evaporation during second period |
Ground water
Subsidence
- Main article: Subsidence (Overlay)
Data
The calculations performed by the water overlay are influenced by many kinds of geographical information present in the project area. For any given location, terrain, constructions and other features can influence either the initial state of the simulation or how water flows in a given area.
Water level area
Attribute | Unit | Description | Default (when attribute is not present) |
WATER_LEVEL | m + datum | The water level for all water terrains in this water level area | n/a |
Sewer area
SEWER_STORAGE | m | The maximum height the water can reach in this sewer. This value, multiplied by the surface area of the sewered constructions the sewer area intersects with, forms the total amount of water this sewer can store. | n/a |
SEWER_PUMP_SPEED | m3/s | The amount of water removed from the sewer by removing it from the hydrological model entirely. | 0 |
Breach
The breach can grow over time, based on its initial width and the critical speed at which water may flow. If a BREACH_WIDTH is defined, the breach's polygon is intersected with a circle emanating from the centerpoint of the polygon. It is only in that intersection, dubbed the "active breach", that water will flow in from the simulated external water body.. The radius of the circle defining the intersection will expand when the water flowing in from the external water body exceeds the BREACH_SPEED. Water flowing in the hydrological model across the breach's surface without explicitly entering or leaving the hydrological model through the breach and its simulated water body does not "count" for the critical speed. All cells in the active breach are considered directly adjacent to the external water body.
The entire breach area is considered lowered to the height defined by its BREACH_HEIGHT attribute, even if the active breach does not extend across the entirety of the breach area.
BREACH_HEIGHT | m + datum | The new terrain height at the location of the breach. | n/a |
BREACH_WIDTH | m | The radius of the breach as drawn on the polygon defining the breach, emanating from the center point. | 10000 |
BREACH_SPEED | m/s | The speed at which water should flow through the breach before the width begins to increase. | n/a |
EXTERNAL_SURFACE_LEVEL | m + datum | The height of the bottom of the external water body behind the breach. The lowest level the external water level can lower to. | 0 |
EXTERNAL_WATER_LEVEL | m + datum | The water level of the external water body behind the breach. The initial level the water level is set to. | 0 |
EXTERNAL_AREA | m² | The surface area of the external water body behind the breach. The larger the external water body, the more water can flow from it, and the smaller the effect of the inflow or outflow of water on the external water level. | n/a |
Inundation
INUNDATION_LEVEL | m + datum | The height of the water. | n/a |
Aquifer
The aquifer is an additional definition for the underground, allowing for underground horizontal flow different from the underground terrain's GROUND_INFILTRATION_MD.
AQUIFER_KD | m²/day | The hydraulic diffusivity of the aquifer, which dictates the speed at which water can flow through the underground. | n/a |
Hydrological constructions
In general, hydrological constructions are loaded in as underground constructions.
- Line-based constructions
Culvert
A culvert is a line-based constructions.
Attribute | Unit | Description | Default |
CULVERT_DIAMETER | m | The diameter of the culvert. For throughput calculations, the culvert is assumed to have a spherical cross-section. | 1 |
CULVERT_THRESHOLD | m + datum | The height of the culvert. (When set to a level lower than the terrain for either endpoint of it, the culvert's height is equal to the height of the (highest) terrain under either endpoint.) | 0 |
CULVERT_N | manning value | The manning value of the culvert's material, which influences the flow speed. | 0,014 |
Weir
A weir is a line-based constructions.
WEIR_HEIGHT | m + datum | The height of the weir. | n/a |
WEIR_WIDTH | m | The width of the weir. | 5 |
WEIR_COEFFICIENT | coefficient | The flow coefficient related to the shape of the weir | 1,1 |
Pump
A pump is a line-based constructions.
PUMP_SPEED | m3/s | The speed at which water is pumped from the lower end-point to the higher end-point. | n/a |
Sewer overflow
A sewer overflow is a point-based constructions. It must intersect with a sewer area, but does not need to intersect with a an actual sewer.
SEWER_OVERFLOW | m + datum | The height of the bottom of the sewer, relative to the average terrain height of the connected sewer. Starting from this height, the water height in the sewer must exceed the height of the terrain at the location of the overflow in order for water to flow out. | n/a |
SEWER_OVERFLOW_SPEED | m3/s | The maximum speed at which water can flow out from the sewer through this overflow. | 10 |
Inlet
An inlet is a point-based constructions.
INLET_Q | m3/sec | The maximum amount of water flowing into the model through this inlet. A negative value means the construction functions as an outlet, and water is removed from the hydrological model. | n/a |
INLET_CAPACITY | m3 | The maximum amount of water which can flow in or out through this construction. Water flowing back in the other direction replenishes the capacity. | Infinite |
LOWER_THRESHOLD | m + datum | If a lower threshold is set, water will only flow into the model through this inlet until the water level at the point of this inlet is equal to or greater than the threshold. If the threshold is not set, the amount of water flowing in is not limited in this fashion. | None |
UPPER_THRESHOLD | m + datum | If an upper threshold is set, water will only flow out the model through this outlet until the water level at the point of this inlet is equal to or lower than the threshold. If the threshold is not set, the amount of water flowing out is not limited in this fashion. | None |
Sewered constructions
Attribute | Unit | Function value | Description |
SEWERED | boolean | Connected to sewer | Whether this construction is connected to the sewer. |
Water storage constructions
WATER_STORAGE | m³/m² | Water storage (m³/m²) | How much water this construction can store. |
Porous constructions
GROUND_INFILTRATION_MD | m/day | Ground infiltration per day (m) | The speed at which water can flow vertically from the surface to the underground unsaturated zone. |
Crops and foliage
Constructions representing crops and foliage can draw water from the underground, allowing it to evaporate. This behaves in the same way as terrain which is configured as plants.
ROOT_DEPTH_M | m | Depth of plant roots (m) | The depth of the roots of this construction, relative to the terrain height at the location of this construction. Water can be drawn from the underground and evaporated if the roots can reach it. |
WATER_EVAPORATION_FACTOR | factor | Water evaporation | How fast this construction can evaporate water from the underground. The weather's evaporation speed is multiplied by this factor to determine the rate of evaporation. |
Critical structures
CRITICAL_INFRASTRUCTURE | nominal integer | Critical infrastructure | Whether this construction is deemed a critical construction. 0 means the construction is never deemed impacted. |
Chemical emitters/decomposers
Chemicals have generic definitions, in terms of name and magnitude, to allow for the modeling of arbitrary substances.
Structures which are defined to create a negative amount of chemicals function as a scrubber or decomposer, removing the specified quantity of chemicals from the hydrological model.
SUBSTANCE_A | x/m² | The amount of substance A created per second per m² in this location. | 0 |
SUBSTANCE_B | x/m² | The amount of substance B created per second per m² in this location. | 0 |
SUBSTANCE_C | x/m² | The amount of substance C created per second per m² in this location. | 0 |
SUBSTANCE_D | x/m² | The amount of substance d created per second per m² in this location. | 0 |
Manning value (construction)
Constructions have an inherent "roughness", which influences how fast water can flow across the surface. This is known as the Manning coefficient or Manning value.
Attribute | Unit | Terrain type | Description |
WATER_MANNING | s/(m1/3) | Surface | The Gauckler–Manning coefficient of the terrain. |
Note that if no construction is present in any location, the WATER_MANNING value of the surface terrain present is used instead.
Construction height
Though not an explicit attribute or function value in and of itself, the height of constructions is taken into account when computing the flow of water above ground. Constructions are computed to have at most a height of DESIGN_FLOOD_ELEVATION_M. Lower constructions retain their own construction height. Taller constructions have their height capped at the attribute's value.
Terrains in a project have a number of hydrological properties which can influence the flow of water in a project. Because there is always both surface and underground terrain defined for the entirety of the project area, all cells are affected by all properties of terrains, unless a construction is present with overwriting values.
Water
Water terrains are processed by the water model in a specific manner before the simulation is started. For each water terrain in the 3D world, the bottom of the water body is treated as a land surface in the same fashion as dry land. Water is then placed on it on the surface layer, up to the level defined by the overlapping water level area's WATER_LEVEL attribute. Terrains not marked as water terrain are not initiated with water.
WATER | boolean | Surface | Whether the specified terrain is a water terrain. |
Plants
Terrains can be configured with plant-related attributes, similar to crops and foliage constructions, allowing it to draw water from the underground and evaporate it.
ROOT_DEPTH_M | m | Surface | The depth of the roots of this surface terrain, relative to the surface. Water can be drawn from the underground and evaporated if the roots can reach it. |
WATER_EVAPORATION_FACTOR | factor | Surface | How fast this terrain can evaporate water from the underground. The weather's evaporation speed is multiplied by this factor to determine the rate of evaporation. |
Also note that the groundwater level reduction is inversely proportional to the WATER_STORAGE_PERCENTAGE, as the contribution of a given volume of water to the groundwater level increases when the capacity for water storage in the underground layer decreases.
Infiltration and storage
GROUND_INFILTRATION_MD | m/day | Surface | The speed at which water can flow vertically from the surface to the underground unsaturated zone. |
GROUND_INFILTRATION_MD | m/day | Underground | The speed at which water can flow vertically from the underground unsaturated zone to the underground saturated zone, and horizontally through across the saturated zone. |
WATER_STORAGE_PERCENTAGE | fraction | Underground | The percentage of the underground volume which can be filled with water. A lower percentage means the underground will be able to store less water, and the saturated zone will rise higher with the same amount of water in the underground layer. |
Manning value (terrain)
Terrains have an inherent "roughness", which influences how fast water can flow across the surface. This is known as the Manning coefficient or Manning value.
Note that if a construction is present in the same location, that construction's WATER_MANNING value is used instead.
Settings
The water overlay features a number of overall settings which can be configured for the hydrological calculations and its results. These settings do not have a geographical or temporal element to them, and are fixed values relevant for the complete simulation.
Result type
Result type | Unit | Display mode | Description |
BASE_TYPES | Nominal value | Start | Categorization of the individual cells based on how they are processed by the water model, displaying which cells are considered to be specific features. 0: Cell on the edge of the project area |
DIRECTION | Degrees | Last | The direction in which water is flowing. |
EVAPORATED | m (mm)¹ | Total | The amount of water that has evaporated. The value is the sum of the quantities evaporated from the surface and the underground. |
GPU OVERVIEW | nominal integer | Maximum | Shows which GPU cluster calculated which part of the overlay. |
IMPACTED_BUILDINGS | nominal integer | Maximum | Constructions impacted by excess water. Constructions are considered impacted when the construction itself or an adjacent cell contains more water on the surface than configured in IMPACT_FLOOD_THRESHOLD_M. 0: Construction is not impacted |
LAST SPEED | m/s | Last | The speed of water flow in any given location. |
MAX SPEED | m/s | Maximum | The speed of water flow in any given location. |
SEWER_LAST_VALUE | m (mm)¹ | Last | The amount of water stored in the sewer. |
SEWER_MAX_VALUE | m (mm)¹ | Maximum | The amount of water stored in the sewer. |
SUBSTANCE_A | x/m² | Last | The amount of substance A present. The value is the sum of the quantities on the surface, and in the underground. |
SUBSTANCE_B | x/m² | Last | The amount of substance B present. The value is the sum of the quantities on the surface, and in the underground. |
SUBSTANCE_C | x/m² | Last | The amount of substance C present. The value is the sum of the quantities on the surface, and in the underground. |
SUBSTANCE_D | x/m² | Last | The amount of substance D present. The value is the sum of the quantities on the surface, and in the underground. |
SURFACE_DURATION | s (min)¹ | Total | The amount of time the water depth on the surface exceeds SHOW_DURATION_FLOOD_LEVEL_M. |
SURFACE_ELEVATION | Description wil be added | ||
SURFACE_FLOW | m³/m² | Description wil be added | |
SURFACE_LAST_VALUE | m (mm)¹ | Last | The amount of water on the surface. |
SURFACE_MAX_VALUE | m (mm)¹ | Maximum | The amount of water on the surface. |
UNDERGROUND_FLOW | m³/m² | Description wil be added | |
UNDERGROUND_LAST_STORAGE | m (mm)¹ | Last | The (effective) amount of water in the underground unsaturated zone. |
UNDERGROUND_LAST_VALUE | m (mm)¹ | Last | The distance between the surface and the groundwater level. |
UNDERGROUND_MAX_STORAGE | m (mm)¹ | Maximum | The (effective) amount of water in the underground unsaturated zone. |
UNDERGROUND_MAX_VALUE | m (mm)¹ | Maximum | The distance between the surface and the groundwater level. |
UNDERGROUND WATERTABLE | m + datum | Last | The groundwater level, relative to datum. |
WATER_STRESS | m (mm)¹ | Maximum | The amount of water on the surface, similar to SURFACE_MAX_VALUE. However, for water terrains, the water level must rise by at least ALLOWED_WATER_INCREASE_M. Otherwise, the reported value in those locations is 0. |
Result child overlays
If a calculation overlay is removed, all result child overlays which are children of that overlay are removed as well. Separate overlays set as child overlays (such as input overlay) of the overlay will not be removed.
It is only possible to add result child overlays via the configuration wizard, in the output overlays step.
Keys
The water model calculations rely on a number of calculation-wide parameters. These parameters are available as attributes of the water overlay and can be modified as such.
ALLOWED_WATER_INCREASE_M | m | The amount by which the water level on a water terrain must increase before it is considered stressed by water. This is used to compute the WATER_STRESS result type. |
DESIGN_FLOOD_ELEVATION_M | m | Constructions in the 3D world are assumed to have at most this height compared to the surface of the terrain. Greater values can create a more accurate model but will impact performance. |
GROUND_BOTTOM_DISTANCE_M | m | Assumed distance under the terrain surface where the soil becomes impenetrable for water. The groundwater level cannot go below this depth, relative to the surface. The maximum amount of water that can be stored underground is equal to this attribute multiplied by the local terrain's WATER_STORAGE_PERCENTAGE. |
GROUND_WATER | boolean | Whether underground water flow is simulated during the calculation. If this is deactivated, surface infiltration, underground infiltration, and underground evaporation do not occur. Water flowing in- and out of the sewer are still simulated when sewers are present. |
IMPACT_FLOOD_THRESHOLD_M | m | The amount of water a construction must experience before it is considered impacted by water. Water must reach this height either on one of the cells the construction is on, or on one of the cells adjacent to it. This is used to compute the IMPACTED BUILDINGS result type. |
MAX_SPEED_MS | m/s | Maximum speed at which water is allowed to flow. This effects the preservation of impulse in water, and as a result the length of computational timesteps. Impulse is more accurately preserved as the maximum speed increases, but will reduce the time per step of the calculation, increasing the total time for the calculation to complete. |
MIN_SLOPE | ratio | The minimum slope required to account for the effect of gravity on the speed of the water. If the slope of the terrain is less than the minimum slope, the effect of gravity on the speed of the water is assumed to be 0. The ratio is the height over distance. |
QUAD_CELL | boolean | This attribute name is reserved for future functionality. Currently, this marks an experimental feature which is currently under development and may result in unexpected behavior when activated. |
SEWER_OVERFLOW_THRESHOLD | fraction | How much of a sewer's storage must be filled with water before the sewer's overflows are allowed to overflow water. |
SHOW_DURATION_FLOOD_LEVEL_M | m | The amount of water which must be present in a specific location before the duration of surface water can be recorded. This is used to compute the SURFACE_DURATION result type. |
SUPERGRID | boolean | This attribute name is reserved for future functionality. Currently, this marks an experimental feature which is currently under development and may result in unexpected behavior when activated. |
SURFACE_WATER_EVAPORATION_FACTOR | factor | The factor by which the weather's evaporation factor is multiplied to compute the amount of evaporation which takes place on the surface. |
TIMEFRAMES | integer | The number of intermediate results recorded during the calculation. Each timeframe becomes a snapshot of data which can be viewed and analysed. The total simulation time is divided by this value, and at each interval of that period of time a snapshot of the results so far is made. Note that the first timeframe does not contain the starting conditions of the simulation, but the state of the simulation after the first period of time has passed. |
Calculations
The water overlay performs a large number of calculations to form a complete hydrological simulation. Depending on the desired viewpoint, both the overarching concepts as well as the implemented formulas can be reviewed for detailed insight into how the water overlay works.
Models
Surface model
The surface is defined by the terrain height in the project. The terrain height is further influenced by the height of constructions present in the project (bounded by DESIGN_FLOOD_ELEVATION_M) and by the BREACH_HEIGHT of breaches.
The surface water level is initialized based on hydrological features present in the project. For all water terrains, water is placed on the surface of the world. The amount of water placed is such that the resulting water level in that location is equal to the WATER_LEVEL attribute of the water level area in that location. If there is no water level area in that location, the water level is assumed to be so low that no water is created. Besides the water level areas, Inundation is added to the model. Water is placed in all locations where inundation is defined (regardless of the terrain type in that location, in contrast to the water level areas), such that the resulting height of the water inundating the land is equal to the inundation area's INUNDATION_LEVEL attribute.
Underground model
The underground water level is initialized with the values of the ground water GeoTIFF connected to the water model. If no ground water data is connected, the ground water level relative to datum is equal to the surface water level relative to datum, as defined by the WATER_LEVEL attribute of the water level area in that location.
When water infiltrates from the surface, it infiltrates at a speed dictated by the surface terrain's GROUND_INFILTRATION_MD attribute, the underground terrain's GROUND_INFILTRATION_MD attribute, or (if present) by the construction's GROUND_INFILTRATION_MD, whichever value is lowest. The least porous material present will always serve as a bottleneck for the water to flow through, even if the other layers allow for a high rate of infiltration.
Rain model
Rain can be implicitly activated and deactivated by defining an appropriate period of rainfall in the weather. If a period with no rainfall is defined, that period is simulated but no rain is simulated.
Evaporation model
Surface evaporation model
Underground evaporation model
Underground evaporation can be implicitly activated or deactivated by setting the relevant properties of all terrain types and constructions to appropriate evaporation values. If the relevant properties are set to 0, no underground evaporation will take place. Underground evaporation is also explicitly deactivated when the underground model is deactivated.
The rate of evaporation is determined by the weather's evaporation rate, and either the construction's WATER_EVAPORATION_FACTOR or the surface terrain's WATER_EVAPORATION_FACTOR.
Sewer model
Storage model
Water on the surface can be stored in water storage constructions.
Chemical flow model
Chemicals are tracked as an exact amount on a given location. The substances are generically defined and do not have a set unit or magnitude.
Chemicals are added to the hydrological model and removed from the hydrological model by chemical emitters and decomposers. The chemicals created are then placed on the surface of the cells where they are created. Chemicals can also be removed by chemical constructions, if their attributes are configured appropriately. When chemicals enter the cell which contains a chemical decomposer, the chemicals are removed from the hydrological model.
When water moves from a cell which also contains chemicals, the chemicals are carried along with the water. The chemicals are uniformly distributed between the water which remains in the cell, which flows to other cells, and which infiltrates. Water which flows into the sewer explicitly cannot carry chemicals along with it.
Model border
The precise calculations which govern the water overlay's simulation are many and varied, and based as much as possible on available expert knowledge.
Timestep formula
- Δt = Δx /umax
Where:
- Δt = computational timestep
- Δx = grid cell size
Surface water level formula
- WLsurface = Wsurface + Hsurface
Where:
- WLsurface = The water level, relative to datum.
- Wsurface = The amount of water (the water column) on the surface.
- Hsurface = The terrain height in the cell, relative to datum.
Surface flow formula
2D Saint Venant
- friction
- bed slope
- water pressure
Groundwater level formula
- WHunderground = Wsat / WSP
- WLunderground = WHunderground + Hsurface - GBDM
Where:
- WLunderground = The groundwater level, relative to datum.
- WHunderground = The height (column) of the saturated zone.
- Wsat = The amount of water in the saturated zone. The height of the water column if the equivalent amount of water was placed on the surface.
Surface infiltration formula
Infiltration capacities:
- Cwater = Wsurface
- Ctop = max( Icon, Isurf )
- Isurf = 0 if a construction is present
- Icon = 0 if no construction is present
Actual infiltration:
- Δw = min( Cwater , Δt * Ctop)
Where:
- Cwater = The amount of infiltration that can take place based on the amount of water on the surface.
- Ctop = The amount of evaporation that can take place based on the infiltration values present.
- Hunsat = Hsurface - WLunderground
- S = Wunsat/Hunsat
- Cinf = min( Hunsat , Δt * Iund )
- Δw = Cinf * S
Where:
- Hunsat = The height of the unsaturated zone.
- S = Ratio of water to height in the unsaturated zone.
- Cinf = The height in the unsaturated zone which can be subject to infiltration to the saturated zone.
- Wunset = The amount of water in the unsaturated zone. The height of the water column if the equivalent amount of water was placed on the surface.
Underground flow formula
- Cd = Δt * Iund * width * A * ( (WLsource - WLtarget) / distance )
- Cd = Δt * Iund * A * (Wsource - Wtarget) / cell
- Cwsp = (WLsource - WLtarget) * (WSPsource / (WSPsource + WSPtarget) )
- Δw = max( 0 , min( Cd , Cwsp ) )
Where:
- Δw = The underground flow which takes place.
- cell = Cell size.
- Cd = The capacity for water flow possible based on the relative water heights.
- Cwsp = The capacity for water flow possible based on the relative water storage percentages.
- WLsource = The amount of water in the saturated zone of the source cell. The height of the water column if the equivalent amount of water was placed on the surface.
- WLtarget = The amount of water in the saturated zone of the target cell. The height of the water column if the equivalent amount of water was placed on the surface.
- A = Contact area of the underground cells
- Iund = The GROUND_INFILTRATION_MD of the underground terrain type of the origin cell.
- WSPsource = The WATER_STORAGE_PERCENTAGE of the underground terrain type of the origin cell.
- WSPtarget = The WATER_STORAGE_PERCENTAGE of the underground terrain type of the target cell.
Culvert formula
Flow through culverts is based on an open channel flow calculation.
- CHreal = max( CHattr , Tleft , Tright )
The height of the water column at either end of the culvert, relative to the culvert, is calculated:
- WHleft = max(0, WLleft-CHreal)
- WHright = max(0, WLright-CHreal)
The loss coefficient for the culvert is calculated:
- U = sqrt( 1.0 / ( 1.0 + 2.0 * G * CN * CN * length / (Rh ^ (4 / 3 ) ) )
The potential flow through the culvert is then calculated:
- C = U * A * sqrt( 2 * G * abs(WHleft - WHright) )
- Δw = Δt * C / cell
Where:
- Δw = The water flow which takes place.
- cell = Cell size.
- C = The potential rate of water flow through the culvert.
- U = Loss coefficient for culverts.
- WHleft = The height of the water column relative to the bottom of the culvert on the left side of the culvert.
- WHright = The height of the water column relative to the bottom of the culvert on the right side of the culvert.
- CHreal = The CULVERT_THRESHOLD of the culvert, recalculated so the culvert is not below ground on either side.
- A = Flow area, based on the height of the water in the (circular) culvert.
- G = Acceleration factor of gravity
- CW = The CULVERT_DIAMETER attribute of the culvert.
- CHattr = The CULVERT_THRESHOLD attribute of the culvert.
- CN = The CULVERT_N attribute of the culvert.
- WLleft = The water level on the left side of the culvert, relative to datum.
- WLright = The water level on the right side of the culvert, relative to datum.
- L = The length of the culvert, calculated as the distance between the culvert's endpoints.
- Rh = The hydrological radius in the culvert[7].
Weir formula
Flow across weirs is calculated differently for free flow and submerged flow.
The height of the water at each end of the weir, relative to the weir, is calculated:
- WHsource = max(0, max( WLleft, WLright ) - WHweir)
- WHdest = max(0, min( WLleft, WLright ) - WHweir)
For free flow, capacity is calculated directly:
- Cfree = DWF * WC * WW * ( WHsource - WHdest )3/2
For submerged flow, a culvert-like calculation is used:
- Csubmerged = U * A * sqrt( 2 * G * (WHsource - WHdest) )
- WHrelative = WHdest : WHsource
- C = min( Csubmerged , Cfree) if WHrelative > 0,5
- C = Cfree otherwise
Where:
- cell = Cell size.
- C = The potential rate of water flow across the weir.
- WHrelative = The ratio of water heights on either side of the culvert.
- Cfree = The potential rate of water flow across the weir, based on a free flow calculation.
- Csubmerged = The potential rate of water flow across the weir, based on a submerged calculation.
- WHsource = The height of the water column relative to the top of the weir, on the side with the highest water level.
- WHdest = The height of the water column relative to the top of the weir, on the side with the lowest water level.
- U = Loss coefficient for submerged weirs (0,9).
- A = Flow area, based on the highest water column height relative to the top of the weir, and the weir width
- DWF = Dutch weir factor, set to 1.7
- WC = The WEIR_COEFFICIENT attribute of the weir.
- WW = The WEIR_WIDTH attribute of the weir.
- WHweir = The WEIR_HEIGHT attribute of the weir.
- WLleft = The water level on the left side of the weir, relative to datum.
- WLright = The water level on the right side of the weir, relative to datum.
Breach growth formula
Breaches can grow when water flows from the virtual external water source into the hydrological model.
First, the difference in height of the water on either side of the breach is calculated.
- H = abs( max(0, Elevel - BH) - max(0, WL - BH) )
Using the height difference, the breach width increase is calculated.
- ΔB = 1.3 * ((G^0.5 * H^1.5) / Uc) * log10 (1 + (0.04 * G / Uc) * Δt / 3600)
The current width is then the result of a running tally of all width increases.
- Bnew = Bold + ΔB
Where:
- B = The total calculated breach width, initially equal to BW.
- ΔB = The calculated width increase of the breach.
- H = The difference between the height of the water columns on either side of the breach.
- MF = Material factor, set to 1.3 (average for sand and clay levees)
- BH = The BREACH_HEIGHT attribute of the breach.
- BW = The BREACH_WIDTH attribute of the breach.
- BS = The BREACH_SPEED attribute of the breach.
- Elevel = Current external water level.
Pump formula
- Δw = min( WHlower , Δt * PS )
Where:
- Δw = The amount water water pumped from the lower to the higher endpoint.
- WHlower = The height of the water column at the lower end of the pump, relative to the terrain.
- PS = The PUMP_SPEED of the pump.
Overflow formula
The amount that can overflow relies on both the sewer overflow itself as well as the sewer overflow threshold:
- Cthreshold = max( 0 , WHsewer - SS * SOT )
- Cheight = max( 0, Tsewer + SO + WHsewer - Toverflow )
- C = min ( Cthreshold, Cheight )
Actual overflow is then calculated:
- Δw = min( 0 , C * Σsewer , Δt * SOS )
- Δw = The amount of sewer overflow which takes place.
- C = The amount of water that can overflow out of the sewer
- Cthreshold = The amount of water that could overflow, based on the sewer overflow threshold.
- Cheight = The amount of water that could overflow, based on the properties of the sewer overflow.
- Σsewer = The surface area of the sewer.
- WHsewer = The height of the water column in the sewer.
- Tsewer = The average height of the terrain where the sewer is present, relative to datum.
- Toverflow = The height of the terrain at the centerpoint of the sewer overflow, relative to datum.
- SO = The SEWER_OVERFLOW attribute of the sewer overflow.
- SOS = The SEWER_OVERFLOW_SPEED attribute of the sewer overflow.
- SS = The SEWER_STORAGE attribute of the sewer area.
- SOT = The SEWER_OVERFLOW_THRESHOLD.
Inlet formula
If a Tlower is defined:
- Cinthres = max( 0 , Tlower - WLsurface )
If a IQ is defined:
- Cspeed = Δt * IQ
If a Ctotal is defined:
- Cincap = Cused - Ctotal
- Δw = max( 0 , min( Cinthres , Cspeed , Cincap ) ) / cell
- If any of the terms are undefined, they are not included.
- Coutthres = min( 0 , Tupper - WLsurface )
If a IQ is defined:
- Cspeed = Δt * IQ
- Coutcap = -Ctotal - Cused
- Δw = min( 0 , max( Coutthres , Cspeed , Coutcap) ) / cell
- Cused (new) = Cused (old) + (Δw * cell)
Where:
- Δw = The amount of water flow which takes place.
- cell = Cell size.
- Cspeed = The amount of water inflow (or outflow when negative) possible based on the inlet's INLET_Q attribute.
- Cincap = The amount of water inflow possible based on the total capacity of the inlet.
- Coutcap = The amount of water outflow possible based on the total capacity of the outlet.
- Cinthres = The amount of water inflow desired based on the inlet's LOWER_THRESHOLD attribute.
- Coutthres = The amount of water outflow desired based on the outlet's UPPER_THRESHOLD attribute.
- WLsurface The water level on the surface, relative to datum.
- Ctotal = The INLET_CAPACITY attribute of the inlet.
- IQ = The INLET_Q attribute of the inlet.
- Tlower = The LOWER_THRESHOLD attribute of the inlet.
- Tupper = The UPPER_THRESHOLD attribute of the inlet.
Surface evaporation formula
- Δw = min( WLsurface , Δt * Eweather * Eoverlay )
Evaporation capacities:
- Csat = max( 0 , min( RD , GBDM ) - Hunsat ) * WSP
- Cunsat = max( 0 , min( RD , Hunsat ) ) * ( Wunsat / Hunsat )
- Δwunsat = min( Cunsat , Δt * Eweather * Etop )
- Δwsat = min( Csat , (Δt * Eweather * Etop) - Δwunsat )
- Δw = Δwunsat + Δwsat
Where:
- Δw = The total amount of evaporation which takes place.
- Δwunsat = The amount of evaporation which takes place from the unsaturated zone.
- Δwsat = The amount of evaporation which takes place from the saturated zone.
- Cunsat = The amount of evaporation that can take place from the unsaturated zone.
- Hunsat = The height (column) of the unsaturated zone.
- Wunsat = The amount of water in the saturated zone. The height of the water column if the equivalent amount of water was placed on the surface.
- RD = The ROOT_DEPTH_M of the construction if present, the ROOT_DEPTH_M of the surface terrain otherwise.
Computational structure
The formulas and concepts come together in a single computational structure which is repeated a large number of times until the total simulation duration has been reached.
Order of operations
- Horizontal surface flow and horizontal underground flow
- Rain
- Building storage
- Sewer inflow
- Surface evaporation
- Groundwater evaporation (saturated zone)
- Groundwater evaporation (unsaturated zone)
- Underground infiltration
- Surface infiltration
- Exfiltration
Calculation time impacts
Warnings
When the water overlay is used and calculations take place, there are some problems or points of attention the calculation can run into. Where possible, the water overlay will show appropriate warnings when running into any issues.
Configuration wizard warnings
While configuring the water overlay using the configuration wizard, each type of data loaded in or found in the project must meet certain requirements to be functional. For example, configured water levels may deviate greatly from the mean terrain height in the project, or certain hydrological constructions may not be shaped appropriately or intersect with required features. In these cases, the configuration wizard will show the warnings in the steps related to the specific type of data.
Inaccurate terrain
When the project is created, the advanced options allow for selecting a high-resolution height map to be loaded in. The default, low resolution height map can introduce artifacts in the calculation due to inaccuracy. This issue can currently only be resolved by reloading the project area.
Calculation halted
If the overlay is recalculated, but the (re)calculation is halted, the water overlay will not contain meaningful results. A warning will be displayed indicating that the calculation did not complete.
Large cell size
The water overlay performs its calculations based on a discretization of the project area. This means both that areas of water are considered a single block, and that obstacles and hydrological properties are averaged out over the extent of a cell. To best approach a realistic, continuous water flow and a realistic model of obstacles and values, it is sufficient to reduce the size of the cells the calculation uses.
- ↑ Jump up to: 1.0 1.1 Kurganov A, Petrova G (2007) ∙ A Second-Order Well-Balanced Positivity Preserving Central-Upwind Scheme for the Saint-Venant System ∙ p 15 ∙ found at: http://www.math.tamu.edu/~gpetrova/KPSV.pdf (last visited 2018-06-29)
- ↑ Jump up to: 2.0 2.1 2.2 Zsolt Horváth, Jürgen Waser, Rui A. P. Perdigão, Artem Konev and Günter Blöschl (2014) ∙ A two-dimensional numerical scheme of dry/wet fronts for the Saint-Venant system of shallow water equations ∙ found at: http://citeseerx.ist.psu.edu/viewdoc/download?doi=10.1.1.700.7977&rep=rep1&type=pdf ∙ http://visdom.at/media/pdf/publications/Poster.pdf ∙ (last visited 2018-06-29)
- ↑ Kurganov A, Petrova G (2007) ∙ A Second-Order Well-Balanced Positivity Preserving Central-Upwind Scheme for the Saint-Venant System ∙ found at: http://www.math.tamu.edu/~gpetrova/KPSV.pdf (last visited 2018-06-29)
- ↑ Langevin, C.D., Hughes, J.D., Banta, E.R., Niswonger, R.G., Panday, Sorab, and Provost, A.M. (2017) ∙ Documentation for the MODFLOW 6 Groundwater Flow Model: U.S. Geological Survey Techniques and Methods, book 6, chap. A55 ∙ p 31 ∙ found at: https://doi.org/10.3133/tm6A55 (last visited 2019-02-04)
- ↑ Hydraulic Radius Equations Formulas Calculator ∙ found at: https://www.ajdesigner.com/phphydraulicradius/hydraulic_radius_equation_pipe.php ∙ (last visited 2019-02-11)